Hi Guys,
John (bogstd),
No problem John I fully appreciate the reason, and thanks for including the text from my original update.
For those that may like some more info, I attach the preceeding document (the one that is updated by the version John posted), this might help put things in better context.
One thing I will add..... the test specifications presented are for COPPER and/or STEEL boilers only.... there is no provision for BRASS boilers under these regulations, it is not an acceptable material in the UK.
They are wholly applicable in the UK and, with few exceptions, for the EU.
Other countries will have their own rules and may even be state dependent (as in the USA), however, they will be broadly similar, so for anyone outside UK/Europe, you will need to get hold of your local regulations.
Florian..... what you say is not quite correct for the UK, here the rule is...if you are the sole user/operator and on PRIVATE land (owned by you) you can use any boiler you like without the need for tast certificates etc, providing no one else is present....if members of the public can also have access then you have an entirely different problem (and this also applies in your own home) in that, in the eyes of the law, the private land is now seen as a PUBLIC place.... and for this you need both A VALID TEST CERTIFICATE, and INSURANCE ..... inside your own home, other members of your family are considered to be THE PUBLIC as far as any claim made on an insurance policy, should an accident occur, INSURANCE would almost cetainly not uphold the claim, and you could actually be prosecuted in law.
If you use, or plan to use your boiler, in a PUBLIC place, then for boilers above the 3 bar/litre capacity, you must hold a valid HYDRAULIC PRESSURE test certificate, and valid STEAM TEST CERTIFICATE.... the latter cannot be obtained without the prior.
Failure to hold both, will exclude you from obtaining VALID insurance, and/or will invalidate any existing insurance until they have been re-obtained....... BE WARNED.
ALAN 2525,
In the extract (posted by Bogs) you will see my comment regarding the STEAM test also being EXEMPT.
Personally, I was surprised they did not make this mandatory for one very good reason...... even a small boiler can become a hazard if it is not operated within it's designed envelope.
Believe me Alan, you would not want to be on the receiving end of even the humble 'MAMOD' small boiler, operating at 15psi- 20psi, let alone a similar size boiler operating at 45psi, should it decide to fail.
Even at 15psi, the contents of the boiler are at 121deg C (249.8deg F) and these would travel a considerable distance (easily 15ft) should a rupture occur..... at 30 psi the temperature would be 134.5deg C (274deg F).... at 45psi temperature would be 144.6deg C (292.4deg F)...... and at 60 psi it would be 153deg C (307.4deg F).... at these higher pressures a small rupture could easily send the contents aver 70ft..... result....if someone is in the line of fire.....DON'T EVEN CONSIDER IT.
Yes, I agree, a SUITABLE safety valve, in conjunction with a small (accurate) pressure gauge should be satisfactory...... the problem is....without undergoing a VALID steam test....how would you, or others around you, KNOW that the safety valve is operating at the correct pressure.
For that matter, how would you know that the safety valve was SUITABLE, or not faulty in some way.
SUITABLE means...... it can safely pass all excess steam generated by the boiler, running at FULL BURNER power, without the pressure in the boiler rising more than 10% over it's normal maximum working pressure.
For a 'MAMOD' running with the normal (supplied) spirit burner, or the solid fuel tablets alternative, then this should not be a problem, providing that the SUPPLIED SAFETY valve is in good working order.
Where a big problem can occur, is when users change over to 'CERAMIC' gas burners (as can be purchased for 'MAMOD' models)........these are far more powerfull than the standard spirit burner, and therefore, it is highly unlikely that the standard SAFETY valve would be able to cope......a more suitable one would need to be installed......this would almost certainly require a modification to be made to the boiler (generally a larger bush would be required)...so now you have a potential problem with safety.
UNLESS you subject the boiler to both HYDRAULIC and STEAM tests.
Finally, some of the early 'MAMOD' boilers were constructed of pretty thin BRASS, (of dubious specification) and were also SOFT soldered.... (later ones are silver soldered, under EU directives)..... this is not suitable for steam temperatures (even at 15psi)..... soft solder becomes malable and loses around 50% - 60% of it's strength at 15psi steam temperature.... failure is not far off.
OK guy's I think that is enough of my drivel for now.
BTW ALAN..... I was BORN in SCOTLAND but raised in WANSTEAD and after I married I moved to HARLOW, where I lived for some 30 years, before escaping back to my HOMELAND..... BRIAN and I go back a long, long way, but that is another long story.
Keep steaming you guys.
;D
Best regards.
SandyC
View attachment Boiler testing in the UK.doc