J J. Tranter Well-Known Member Joined Jul 8, 2007 Messages 126 Reaction score 0 Dec 2, 2009 #1 When pressure testing a boiler how long do you leave it under pressure? Thank you John Tranter
Jasonb Project of the Month Winner!!! Project of the Month Winner Joined Mar 30, 2008 Messages 3,810 Reaction score 1,289 Location Surrey, UK Dec 2, 2009 #2 In the UK the boiler should be held at twice working pressure for a minimum of 10 mins, or however long it takes to inspect for signs of leakage. Make sure the boiler is full of water not air and raise the pressure no more than 10% at a time once above working pressure. Jason
In the UK the boiler should be held at twice working pressure for a minimum of 10 mins, or however long it takes to inspect for signs of leakage. Make sure the boiler is full of water not air and raise the pressure no more than 10% at a time once above working pressure. Jason
J J. Tranter Well-Known Member Joined Jul 8, 2007 Messages 126 Reaction score 0 Dec 2, 2009 #3 Thank you for the reply I greatly appreciate it. John Tranter